Prepare for the Master Electrician Exam with detailed practice quizzes and study resources. Improve your knowledge with multiple-choice questions that cover key concepts and practical applications. Get ready to excel in your certification!

Practice this question and more.


What is the maximum standard size overcurrent protection device permitted on the primary side of a 50 kVA transformer with a 480-volt, 3-phase primary?

  1. 80 amperes

  2. 100 amperes

  3. 125 amperes

  4. 150 amperes

The correct answer is: 150 amperes

To determine the maximum standard size overcurrent protection device permitted on the primary side of a 50 kVA transformer with a 480-volt, 3-phase primary, one must first calculate the full-load current of the transformer. The formula used is: Full-load current (I) = kVA × 1000 / (Voltage × √3) For a 50 kVA transformer at 480 volts, the calculation would be: I = 50 × 1000 / (480 × √3) Calculating √3 gives approximately 1.732, thus: I = 50000 / (480 × 1.732) I ≈ 50000 / 831.36 I ≈ 60.1 amperes According to the National Electrical Code (NEC), for transformers, overcurrent protection on the primary side can be sized larger than the full-load current by using the 125% rule for overcurrent protection for transformers rated above 9 kVA. Thus, the size of the overcurrent protection device can be calculated as follows: 125% of full-load current = 1.25 × 60.1 amperes ≈ 75.125 amperes The next step is